GFCI Troubleshooting - Housewiring Question HELP NEEDED (1 Viewer)

Pure Energy

Rethink Everything
Joined
Aug 24, 2002
Messages
10,950
Reaction score
10
Location
Somerset County NJ (via St. Mary Parish)
Offline
GFCI is resetting itself; I've unplugged everything I can find on the circuit. It still won't stay set. This happened a few years ago and the culprit was the sump-pump. I bought a new sump pump and the electrician wired the pump on a separate breaker.

My plan is to do a real quick trouble-shoot of the GFCI by swapping it out with the one downstairs; but I'm reasonably confident the GFCI is good but will go through the motions to eliminate this possibility.

If this isn't it; I'm pretty much out of ideas. Any help with this issue is appreciated. The only significant variable that has changed is the deluge of ice, rain and snow over the past 18 hours. We're under a flood watch.
 

Thorin

Idle
Joined
Dec 9, 2006
Messages
7,800
Reaction score
957
Age
48
Location
Shreveport, Tx.
Offline
You're on the right track, swap the GFCI and post the results.

EDIT: also, if you expect water intrusion, open the feed breaker, get an ohmmeter, and check the resistance from ground to the hot and neutral wires. If it doesn't read open, you will have to find the short.
 
Last edited:

Devildog

Meh
Joined
Feb 26, 2004
Messages
17,356
Reaction score
20,000
Age
47
Location
:hookthem:
Offline
Well it's not a GFCI problem. The other tripped.

Thorin, could the short be in a defective breaker?


It could be. Are the 2 GFCI's on the same circuit? If so, have you checked the breaker to see if it's tripped? Mine did that a couple of years ago where it would get hot and the thermal protector in my breaker would trip it off line. I would have to go reset it and it would do it about once a day. I replaced it and haven't had any problems since.
 

Thorin

Idle
Joined
Dec 9, 2006
Messages
7,800
Reaction score
957
Age
48
Location
Shreveport, Tx.
Offline
If the feed breaker were shorted you would probably have more catastrophic problems, like fire. If you know the full path of the circuit, start disconnecting the fixtures / outlets . Connect the gfci as close to the feed as you can get see it it still pops. If it holds, work your way out from there. If you get to a point that it starts tripping again, you have then isolated it down to a much smaller area. If the problem is water intrusion, it might dry out before you actually find the problem.
 
OP
Pure Energy

Pure Energy

Rethink Everything
Joined
Aug 24, 2002
Messages
10,950
Reaction score
10
Location
Somerset County NJ (via St. Mary Parish)
Offline
They're on different circuits and the breaker that the GFCI's are tripping requires frequent reset (~4 time s a year).

How difficult (dangerous) is it to replace a breaker? Do I have to cut power to the entire house to do it?
 

Thorin

Idle
Joined
Dec 9, 2006
Messages
7,800
Reaction score
957
Age
48
Location
Shreveport, Tx.
Offline
They're on different circuits and the breaker that the GFCI's are tripping requires frequent reset (~4 time s a year).

How difficult (dangerous) is it to replace a breaker? Do I have to cut power to the entire house to do it?

Yes, be careful, there is usually a service disconnect switch outside or a main on the circuit breaker panel that feeds the smaller breakers. I always check a circuit with a voltmeter before I touch it just to be sure.
 
OP
Pure Energy

Pure Energy

Rethink Everything
Joined
Aug 24, 2002
Messages
10,950
Reaction score
10
Location
Somerset County NJ (via St. Mary Parish)
Offline
If the feed breaker were shorted you would probably have more catastrophic problems, like fire. If you know the full path of the circuit, start disconnecting the fixtures / outlets . Connect the gfci as close to the feed as you can get see it it still pops. If it holds, work your way out from there. If you get to a point that it starts tripping again, you have then isolated it down to a much smaller area. If the problem is water intrusion, it might dry out before you actually find the problem.

Gotcha....I've identified the 5 outlets on the circuit (2 in each bathroom and one in the basement). The closest is in the basement.

Note: I'm taking the day off from work to trouble-shoot this problem--I need a day away from the office anyway. :)
 

Thorin

Idle
Joined
Dec 9, 2006
Messages
7,800
Reaction score
957
Age
48
Location
Shreveport, Tx.
Offline
Gotcha....I've identified the 5 outlets on the circuit (2 in each bathroom and one in the basement). The closest is in the basement.

Note: I'm taking the day off from work to trouble-shoot this problem--I need a day away from the office anyway. :)

Just for clarification, be sure to disconnect the romex that is further down the line as you move the GFCI around, effectively starting with a small circuit, and getting longer as you move down the line.
 

Taurus

More than 15K posts served!
VIP Contributor
Joined
Dec 20, 1997
Messages
26,258
Reaction score
16,362
Age
53
Location
Yacolt, WA
Offline
(tongue in cheek)

All I know is that there is no such thing in the world as a competent electrician. Every single one I've ever hired has looked at the current wiring and said "What the hell was that last guy thinking?"
 

efil4stnias

Play at your own risk
Joined
Jul 9, 2001
Messages
34,585
Reaction score
34,649
Location
Covington
Offline
GFCI is resetting itself; I've unplugged everything I can find on the circuit. It still won't stay set. This happened a few years ago and the culprit was the sump-pump. I bought a new sump pump and the electrician wired the pump on a separate breaker.

My plan is to do a real quick trouble-shoot of the GFCI by swapping it out with the one downstairs; but I'm reasonably confident the GFCI is good but will go through the motions to eliminate this possibility.

If this isn't it; I'm pretty much out of ideas. Any help with this issue is appreciated. The only significant variable that has changed is the deluge of ice, rain and snow over the past 18 hours. We're under a flood watch.



I have a similar problem in my garage with out lamp post out front. After a HEAVY rain, water will intrude and soak the bulb/bulb holder and will cause my GFI to trip. Got home last night, hit the garage opener and knew right away what needed to be done. I have to remove lamnp cover, remove bulb, dry bulb and the bulb holder of any water, replace and press reset. I have completely caulked the interior of the lamp cover, sealed the lamppost and still get water INSIDE the doggone thing. Now I am thinking the underground wiring is not in a conduit and somehow getting moisture after a heavy rain.

Good luck....
 

Redlands Saints

killing threads daily
VIP Subscribing Member
Gold VIP Contributor
Joined
Sep 9, 2005
Messages
4,056
Reaction score
465
Location
Redlands, CA
Offline
I have a similar problem in my garage with out lamp post out front. After a HEAVY rain, water will intrude and soak the bulb/bulb holder and will cause my GFI to trip. Got home last night, hit the garage opener and knew right away what needed to be done. I have to remove lamnp cover, remove bulb, dry bulb and the bulb holder of any water, replace and press reset. I have completely caulked the interior of the lamp cover, sealed the lamppost and still get water INSIDE the doggone thing. Now I am thinking the underground wiring is not in a conduit and somehow getting moisture after a heavy rain.

Good luck....

the wire could be in conduit and still get wet. if its old or when they pulled it they damaged the jacket it could be getting wet and shorting out to the conduit.
 

Devildog

Meh
Joined
Feb 26, 2004
Messages
17,356
Reaction score
20,000
Age
47
Location
:hookthem:
Offline
(tongue in cheek)

All I know is that there is no such thing in the world as a competent electrician. Every single one I've ever hired has looked at the current wiring and said "What the hell was that last guy thinking?"


I do that where I work. I am in the apprentice program for electrician for an offshore drilling company and you would be amazed at the shoddy workmanship some of those electricians have left behind.:covri:
 

efil4stnias

Play at your own risk
Joined
Jul 9, 2001
Messages
34,585
Reaction score
34,649
Location
Covington
Offline
the wire could be in conduit and still get wet. if its old or when they pulled it they damaged the jacket it could be getting wet and shorting out to the conduit.

dang so I would have to dig up the conduit to check the wiring. Thats about right for me....
 

Redlands Saints

killing threads daily
VIP Subscribing Member
Gold VIP Contributor
Joined
Sep 9, 2005
Messages
4,056
Reaction score
465
Location
Redlands, CA
Offline
dang so I would have to dig up the conduit to check the wiring. Thats about right for me....

well if you want to find out if there is water in the pipe carefully put a shop vac hose from the exhaust side of the vac on the conduit at the electrical panel and see if you blow water out the other side at the light pole. shut the power off on that circuit first. if you have a multi-meter you could shut off the circuit and check to see if you have continuity between the power wire and ground or common.
 